You are fine to go 40A with your wiring. Metal conduit will dissipate heat and THHN insulation has a higher temp rating.Luckyduckie said:The electrician who installed my 32A Aerovironment EVSE told me that it was ok to have #8 THHN in conduit for NEMA 14-50 with a 50A breaker. I might be getting the juicebox; should I go for the 40A or just stick to 32A to be safe??
If you leave the 50A breaker it is sure to be safe. If you only charge vehicles like the RAV that only pull up to 40A you will never have any problem. If you plug in a Model S that has dual chargers, it may pop the breaker after a while - maybe 30 minutes or so. Personally, with #6 Romex (NMB type) I would leave the 50A breaker and not increase it to 60.Rav4EVoom said:I just installed my hcs-60. I had Romex with #6 wire from panel to 14-50outlet on 50amp breaker.(since rav4ev only pull upto 40amp). the hcs-60 comes with #8 wire for both input cord and output cord. (I had added a 14-50 male plug on it.) So I assume #6 for my receptacle should be OK. So far I am charging my rav4ev without issue.
Rav4EVoom said:I just installed my hcs-60. I had Romex with #6 wire from panel to 14-50outlet on 50amp breaker.(since rav4ev only pull upto 40amp). the hcs-60 comes with #8 wire for both input cord and output cord. (I had added a 14-50 male plug on it.) So I assume #6 for my receptacle should be OK. So far I am charging my rav4ev without issue.
49erRAV said:Rav4EVoom said:I just installed my hcs-60. I had Romex with #6 wire from panel to 14-50outlet on 50amp breaker.(since rav4ev only pull upto 40amp). the hcs-60 comes with #8 wire for both input cord and output cord. (I had added a 14-50 male plug on it.) So I assume #6 for my receptacle should be OK. So far I am charging my rav4ev without issue.
I wanted to do the exact same thing, but Clipper Creek explicitly advised against doing so.. They said they required a 60A circuit (and breaker) for the HCS-60. Glad to hear it's working just fine though, but thought I'd let you know CC's stance on it..